Found this site after I’ve about lost my mind trying to solve my elderly mother’s gas fireplace...
U-43 Regency is the fireplace/stove and it’s about 23 years old. It’s been good for all those years but this year it’s having problems.
Best I can tell from family reports is that it shuts off for no known reason usually overnight, and will not fire up again until being “manipulated” later.
Pilot light never goes out, is good and strong. Thermocouple seems to appear fine, but thermopile ended up being low so I replaced it and the MV readings are constantly good (500-600 millivolts) Everything cleaned too. Last year I wired in a basicMV thermostat and it did fine. The chimney where it’s vented to is clear as well...
The manual that came with it is not exactly matched with it as far as wiring. I did find one online that had a more exact diagram (3 position switch for “auto”, middle off, and down for ON manual mode. I replaced the switch as well...
After so many trips and testing I’m concerned that it could be the valve. (SIT 820–original manual says it’s a Robert Shaw and that’s wrong). As I said, the pilot always stays on, the thermopile puts out the needed voltage, and the thermostat checks out fine as well. (Yesterday, when I got there the stat was calling for heat but nothing happening. I metered the contact screws and still the correct voltage was there) Done some finagling and it finally started, only to shuts down a few hours later.)
Also, I’m thinking I have thermostat wiring wrong (odd that it worked this way last year) as instead of having one lead on the top screw (TH). Both have been installed on the bottom and middle screws for a couple years now. I tried on lead on that TH and NOTHING would happen. The “pile” leads are on bottom and middle. And then again I’m still not sure that a wiring mistake elsewhere hasn’t been made...
Any ideas?
Thanks much.
U-43 Regency is the fireplace/stove and it’s about 23 years old. It’s been good for all those years but this year it’s having problems.
Best I can tell from family reports is that it shuts off for no known reason usually overnight, and will not fire up again until being “manipulated” later.
Pilot light never goes out, is good and strong. Thermocouple seems to appear fine, but thermopile ended up being low so I replaced it and the MV readings are constantly good (500-600 millivolts) Everything cleaned too. Last year I wired in a basicMV thermostat and it did fine. The chimney where it’s vented to is clear as well...
The manual that came with it is not exactly matched with it as far as wiring. I did find one online that had a more exact diagram (3 position switch for “auto”, middle off, and down for ON manual mode. I replaced the switch as well...
After so many trips and testing I’m concerned that it could be the valve. (SIT 820–original manual says it’s a Robert Shaw and that’s wrong). As I said, the pilot always stays on, the thermopile puts out the needed voltage, and the thermostat checks out fine as well. (Yesterday, when I got there the stat was calling for heat but nothing happening. I metered the contact screws and still the correct voltage was there) Done some finagling and it finally started, only to shuts down a few hours later.)
Also, I’m thinking I have thermostat wiring wrong (odd that it worked this way last year) as instead of having one lead on the top screw (TH). Both have been installed on the bottom and middle screws for a couple years now. I tried on lead on that TH and NOTHING would happen. The “pile” leads are on bottom and middle. And then again I’m still not sure that a wiring mistake elsewhere hasn’t been made...
Any ideas?
Thanks much.