Hello all It's been ages since I've been on here but I'm currently planning to install a Froling S30 wood boiler along with 400 gallons of storage. It will be located in my detached garage/shop. I reaching out to see if I've missed anything or improvements I could make.
Question 1: I live in Kentville, Nova Scotia, Canada does anyone out east have a leed on a storage tank 400+ gallons? or where I can pick one up? I've been looking for the past year and have had little luck in finding something used (Including propane tanks). If I have to I've allowed for buying one new.
Question 2: Pipe size for the main run. From the garage to the house is about 45'-50' underground. I ballpark from boiler to the distribution header in the house to be about 75'-100' Should I go with 1" or 1-1/4" I was thinking 1-1/4 for less head loss and more flow if needed in the future.
The current plan is to use 5 circulators labeled 1, 3, 4, 5 and 7 I was going to use all Alpha2, 15-55's (except for the domestic loop) There is an efficiency rebate and they cost about the same as a standard circ. The boiler and storage will be right next to one another. So I should be able to see 10 gpm flow. The boiler protection was going to be a caleffi ThermoProtec 280 valve.
Circ 3 Will heat the shop and when the garage is redone do the infloor loop.
Circ 4 is located in the garage and will run when zones call for heat. So pex size 1" or 1-1/4" with the Alpha2 15-55?
The main load for the house is the air handler it heats the 1000sqft basement (will be redone with infloor 5+ years) and the main level 1000sqft. We also have a full 2nd story but don't turn the heat on up there as the heat from the main level is enough to keep it warm.
The current infloor loop (200sqft) is my mother in laws room. We re did it and I added the infloor heat. It's currently being headed with my home made electric boiler I dont have the air traps shown but other than that anything I'm missing or changes you'd make? I look forward to reading your comments.
(Edit) The boiler protection loop isn't run separately to the storage it just tee's above it's self and the two water to air heat exchangers will be plumbed for even flow.
Question 1: I live in Kentville, Nova Scotia, Canada does anyone out east have a leed on a storage tank 400+ gallons? or where I can pick one up? I've been looking for the past year and have had little luck in finding something used (Including propane tanks). If I have to I've allowed for buying one new.
Question 2: Pipe size for the main run. From the garage to the house is about 45'-50' underground. I ballpark from boiler to the distribution header in the house to be about 75'-100' Should I go with 1" or 1-1/4" I was thinking 1-1/4 for less head loss and more flow if needed in the future.
The current plan is to use 5 circulators labeled 1, 3, 4, 5 and 7 I was going to use all Alpha2, 15-55's (except for the domestic loop) There is an efficiency rebate and they cost about the same as a standard circ. The boiler and storage will be right next to one another. So I should be able to see 10 gpm flow. The boiler protection was going to be a caleffi ThermoProtec 280 valve.
Circ 3 Will heat the shop and when the garage is redone do the infloor loop.
Circ 4 is located in the garage and will run when zones call for heat. So pex size 1" or 1-1/4" with the Alpha2 15-55?
The main load for the house is the air handler it heats the 1000sqft basement (will be redone with infloor 5+ years) and the main level 1000sqft. We also have a full 2nd story but don't turn the heat on up there as the heat from the main level is enough to keep it warm.
The current infloor loop (200sqft) is my mother in laws room. We re did it and I added the infloor heat. It's currently being headed with my home made electric boiler I dont have the air traps shown but other than that anything I'm missing or changes you'd make? I look forward to reading your comments.
(Edit) The boiler protection loop isn't run separately to the storage it just tee's above it's self and the two water to air heat exchangers will be plumbed for even flow.