NewtownPA said:
I bought my house with the wood stove already installed. Just last week I discovered that my stove has a 6" output which goes to an oval pipe about 6 feel long and then merges with a 12x8 masonry chimney.
I was talking to the chimney cleaning company and they said that in it's current configuration its:
1. Not up to code
2. Not as efficient as it should be
3. Results in more creosote
Let me try to answer these questions fully - to some level.
First of all, have you used the stove extensively? How does it burn?
OK, I am going to go backwards and start with #3...
Results in more creosote:
The answer to this is the amount of creosote that is in the chimney. I have installed many hundreds of Avalons into similar situations with similar piping, and our sweeps have almost always reported that they get almost NO creosote out when cleaning...and perhaps less than a gallon can of soot and loose particles (which pose no ignition danger).
So, unless you have seen for yourself that you have a lot of black tar creosote from this stove, I would question this assumption.
Not as Efficient
This relates also to how the stove operates for you. If the stove burns well at most levels of operation, then it is burning efficiently. Efficiency relates to the wood, the operator, the stove and the chimney. It is also a hard EXACT figure to put your head around. In other words, if you stove was burning at 2% less efficient than it "might", is that classified as "not as efficient". On both these questions, the proof is in the pudding.
Not up to Code
First, check your owners manual and see if the stove was installed in the fashion required there. After that point, we can consult the NFPA code which was in effect at the time of your installation - chances are that was the previous version of NFPA 211 - the new one is just getting distributed recently.
That version would state (I think) that the masonry chimney cross-section should not be more than 3x the size of the pipe if the fireplace chimney was outside, and 4x if the chimney was inside. Your chimney is somewhere in between, since it appears it may be in a garage or other room for part of the run.....
An 8x12 chimney is usually about 6.5 x 10.5 ID, which is about 70 Square inches of flue area. A 6" pipe is:
pie x (times) the radius squared, or about 28 square inches, meaning that your installation would pass the previous version of NFPA.
The brand new version of NFPA211 has taken the figures down to 2x if chimney is exterior, and 3x if the chimney is interior. So depending on exactly how an inspector would classify your chimney - it would pass current standards if interior, and not quite if exterior.
Chimneys do not have to be "upgraded" to current code changes, but new installations must follow these standards.
All in all, the biggest question is how well the stove starts and operates, and how clean the chimney stays.
Summary - your installation is probably approved by the manufacturer and test lab as per the manual and probably also kosher as to when it was installed. It would easily pass muster from 1979 to 2006......but as a NEW installation, it would depend on whether the chimney was classified interior or exterior as to whether it would meet NFPA 211.