Been scouring the web for a few hours and have been unable to find the troubleshooting information I need, hoping you fine folks can help me out...the Jotul manual certainly isn't very forthcoming with helpful information or diagrams.
I have a Jotul GF3 BV that was working fine a week ago. I turned the pilot off when I went on vacation for a week, came back and can't get the pilot to light!
I measured the TC at ~14mv so I went ahead and changed it out, now I'm getting ~30mv so I think that should be OK. I checked the thermopile and was able to get up to ~550mv after 60 seconds or so, so I think thats okay as well.
Now, I somehow completely over looked that one wire from the spill switch was dangling on the floor, I think it must have become brittle and been yanked off by the cats or something. Will the spill switch prevent the pilot from lighting or only the main burner?
Can someone help me identify where the spill switch should be connected? I can't for the life of me figure out where it should have been connected. In the attached image you can see the wire dangling below center, it had a terminal of some sort attached to it but it must have become brittle and broken off.
I believe the wire bundle dangling to the lower left are for the optional blower, they have never been connected to anything so I have just been ignoring them.
Been scouring the web for a few hours and have been unable to find the troubleshooting information I need, hoping you fine folks can help me out...the Jotul manual certainly isn't very forthcoming with helpful information or diagrams.
I have a Jotul GF3 BV that was working fine a week ago. I turned the pilot off when I went on vacation for a week, came back and can't get the pilot to light!
I measured the TC at ~14mv so I went ahead and changed it out, now I'm getting ~30mv so I think that should be OK. I checked the thermopile and was able to get up to ~550mv after 60 seconds or so, so I think thats okay as well.
Now, I somehow completely over looked that one wire from the spill switch was dangling on the floor, I think it must have become brittle and been yanked off by the cats or something. Will the spill switch prevent the pilot from lighting or only the main burner?
Can someone help me identify where the spill switch should be connected? I can't for the life of me figure out where it should have been connected. In the attached image you can see the wire dangling below center, it had a terminal of some sort attached to it but it must have become brittle and broken off.
I believe the wire bundle dangling to the lower left are for the optional blower, they have never been connected to anything so I have just been ignoring them.