Hello All,
I found this forum after research what I thought was my problem. Here it is: I have the Jotul Allagash 3.
I can light the pilot and it will stay on. I left it on for 2 days no problem. Then I turned on the main burner and after 20 to 30 minutes both the main and pilot flame dropped out.
At which time I took the stove apart and cleaned the thermocouple and thermopile. I checked the pilot orfice and cap. I also tightened the thermopile in the housing. Also checked the main burner orfice. Then put it all back together.
So I did the millivolt test. Thermopile readings from a cold start went to 650 and dropped back to a maintained value of 567. Then after firing up the main it dropped to 260 and maintained at 246, eventually dropping to 210. Then I used the wall thermostat to control the burner and the reading went up to 232.
I ran it for 1 1/2 hours and had no problems. Thinking that I had it fixed I turned off the main burner. Ten minutes later I heard a click and checked to see the pilot light had dropped out. At that point the millavolt reading was 400.
Can anyone tell if it is the thermocouple or the thermopile?
Thanks in advance for any info.
kc classic
I found this forum after research what I thought was my problem. Here it is: I have the Jotul Allagash 3.
I can light the pilot and it will stay on. I left it on for 2 days no problem. Then I turned on the main burner and after 20 to 30 minutes both the main and pilot flame dropped out.
At which time I took the stove apart and cleaned the thermocouple and thermopile. I checked the pilot orfice and cap. I also tightened the thermopile in the housing. Also checked the main burner orfice. Then put it all back together.
So I did the millivolt test. Thermopile readings from a cold start went to 650 and dropped back to a maintained value of 567. Then after firing up the main it dropped to 260 and maintained at 246, eventually dropping to 210. Then I used the wall thermostat to control the burner and the reading went up to 232.
I ran it for 1 1/2 hours and had no problems. Thinking that I had it fixed I turned off the main burner. Ten minutes later I heard a click and checked to see the pilot light had dropped out. At that point the millavolt reading was 400.
Can anyone tell if it is the thermocouple or the thermopile?
Thanks in advance for any info.
kc classic