If a chimney is specified as ULC-S629 listed (Canada requirements), but says nothing about being UL-103HT listed (US requirements), do the US building codes recognize it anyway as being UL-103HT compliant?
I understand the Canada ULC-S629 actually sets a higher standard than the US's UL-103HT. I understand the ULC-S629 requires withstanding three, 30 minutes burns at 2100 degrees.
The US's UL-103HT only requires the chimney withstand three, 10 minute burns at 2100 degrees.
So, if a product is "listed" as ULC-S629 compliant, but is silent as to UL-103HT, is it approved for US installation anyway? Does US building codes recognize ULC-S629 as inclusive of UL-103HT?
Or will US inspectors demand to see the chimney company say in writing "UL-103HT" compliant? And ignore the writing that says "ULC-S629" compliant.
builderbob
	
		
			
		
		
	
				
			I understand the Canada ULC-S629 actually sets a higher standard than the US's UL-103HT. I understand the ULC-S629 requires withstanding three, 30 minutes burns at 2100 degrees.
The US's UL-103HT only requires the chimney withstand three, 10 minute burns at 2100 degrees.
So, if a product is "listed" as ULC-S629 compliant, but is silent as to UL-103HT, is it approved for US installation anyway? Does US building codes recognize ULC-S629 as inclusive of UL-103HT?
Or will US inspectors demand to see the chimney company say in writing "UL-103HT" compliant? And ignore the writing that says "ULC-S629" compliant.
builderbob
 
	 
	 
 
		 
 
		 !! thats a great question , i'll get the answer within a few days from contact at simpson , i need to call her anyway. will post here when i speak to her and get answer
!! thats a great question , i'll get the answer within a few days from contact at simpson , i need to call her anyway. will post here when i speak to her and get answer 
 
		 
 
		 
 
		 
 
		 
 
		 
 
		 
 
		