I had a Vermont Castings small winter warmer professionally installed 4 years ago. Chimney sweep is telling me liner needs to be insulated.......true or no? I have it cleaned annually to avoid a lot of build-up. Thanks!
Doubtful, I bet they have either have an excessive amount of creosote or they have a breeched clay liner. Not much money in pulling a liner to insulate, in my opinion.k3c4forlife said:Or he is looking to get paid to install it. As a general rule of thumb, they help in pretty much every way. I will be insulating a Regency Insert chimney liner on an interior chimney.
hilbrad said:He is saying it is required by code, but both the installer and vendor say nonsense. I am currently waiting for an answer from the building inspector, but it was installed without a permit so I am trying to keep it on the DL. Installer said it (permit) was not required. I have had no problems with it, and the chimney was rebuilt from the roofline up about 2 years ago. Problem is I am not sure if chimney itself is lined or not.....need to get back to the mason for that info. I wish I had been a bit more educated then, and would have known what questions to ask!
Thanks for your help!
We don't know if it has to be insulated, Being interior has little to do with it. If the flue is compromised it has to be insulated.CK-1 said:hilbrad said:He is saying it is required by code, but both the installer and vendor say nonsense. I am currently waiting for an answer from the building inspector, but it was installed without a permit so I am trying to keep it on the DL. Installer said it (permit) was not required. I have had no problems with it, and the chimney was rebuilt from the roofline up about 2 years ago. Problem is I am not sure if chimney itself is lined or not.....need to get back to the mason for that info. I wish I had been a bit more educated then, and would have known what questions to ask!
Thanks for your help!
If the chimney was rebuilt from the roofline up then it sounds like this is a interior chimney. If so, the liner doesn't need to be insulated.
jtp10181 said:Unless the masonry chimney structure passes a Level II inspection (meeting NFPA 211 guidelines) then the liner must be insulated. Such an inspection would require visually inspecting the masonry structure from top to bottom where it comes in contact with the house, verifying all clearances are met. Also would need to verify the proper air gap from the clay tiles to the masonry block, as well as the integrity of the clay tiles themselves. If any one thing does not pass, it fails.
Without insulation the SS liner serves only to reduce your flue size, it adds absolutely no safety factor if you were to have a chimney fire. A 2000F chimney fire would heat up all the masonry so much that if there is combustibles up against it, lets say in the attic, your roof would probably catch on fire. Furthermore, all liners I have seen, with no insulation you are required to have 1" spacers on the liner to keep it from resting right up against the clay tiles. This is rarely done.
Adding the insulation, the liner should then meet UL1777 specs, which allows the insulated liner to be touching the clay tiles, and also allows the masonry structure as a whole to be touching combustibles.
So, knowing all this, as a dealer it is far easier to just insulate every liner we do and not have to worry about anything.
You might notice I used words like "should" and "may". This is because each liner system is tested independently and could have different requirements. For the most part they are all the same, but each mfg has their own instructions that should be followed.
I think your installer needs to read some install manuals, NFPA code books, and the UL1777 listing.