This question, more like situation, has come up more often then not around here, and also on the retail sales floor. Ironic i got a tech bulliten today from one of my manufactures that outlines the requirements.
Some companies have "blanket" listings for all there stoves and inserts they manufacture and sell. With that any single one of there stoves can be installed in a zero clearance fireplace.
Even though leagle, there are issues with this install, mostly that ZC fireplaces are to short, and you still have to maintain the clearance to the fireplace like it was a combustable, which will result in a long horizontal run.
Here is the 10 point list of requierments:
1) The insert must be tested to UL 1482 or ULC S628
2) The FIREPLACE must be tested to UL627 or ULC S610
3) Clearances from masonry fireplace testing are also relevant for installations in a factory built fireplace.
4) The chimney liner must meet the "HT" requirements
5) Room air must be blocked from entering the chimney cavity (usally by blocking the damper area OR sealing the fireplace front.)
6) Louvers or cooling inlets must not be blocked
7) Alteration of the fireplace is not permitted unless specific exceptions are listed in the owners manual.
8) Circulating air chambers must not be blocked
9) Means to remove the insert for cleaning must be provided
10) A permanent metal warning lable saying that the fireplace must be restored to its original condition if the insert is removed.
Food for thought....
Some companies have "blanket" listings for all there stoves and inserts they manufacture and sell. With that any single one of there stoves can be installed in a zero clearance fireplace.
Even though leagle, there are issues with this install, mostly that ZC fireplaces are to short, and you still have to maintain the clearance to the fireplace like it was a combustable, which will result in a long horizontal run.
Here is the 10 point list of requierments:
1) The insert must be tested to UL 1482 or ULC S628
2) The FIREPLACE must be tested to UL627 or ULC S610
3) Clearances from masonry fireplace testing are also relevant for installations in a factory built fireplace.
4) The chimney liner must meet the "HT" requirements
5) Room air must be blocked from entering the chimney cavity (usally by blocking the damper area OR sealing the fireplace front.)
6) Louvers or cooling inlets must not be blocked
7) Alteration of the fireplace is not permitted unless specific exceptions are listed in the owners manual.
8) Circulating air chambers must not be blocked
9) Means to remove the insert for cleaning must be provided
10) A permanent metal warning lable saying that the fireplace must be restored to its original condition if the insert is removed.
Food for thought....