I have a Innova 30 w/ square tank(820gal) that's on Tarm website. Neat looking HX's. Controls and valves are also supplied by Tarm. Termovar Loading valve option.Installed system as their diagram shows. Followed instructions on starting a fire and lit the kindling and 1 to 2 minutes later loading wood and shut door. Had gasification very quickly.Stack temp has run pretty steady 400.
I have a 1800 sq/ft 2 story house, built about 12 yrs ago. Standard insulation. Located on a hill and we had -18 below with about 7 to 10 mph wind. Shut down heating zones( 2 zones) in house while wiring in BLT control and other related equipment. Probably had house offline for about 2 hours, from about 11pm to 130am. Once turned back on, zones called for heat all the time, while heating the storage. Also I located my boiler in an unattached garage aprox 40ft away, had a total run of 40ft underground and 60ft in buildings. Don't have all my notes with me, but I filled it at various times, not full each time, but I probably filled it complete about 4 times? I filled it last about 7am this morning, put too much wood in,fan shut down a couple of times, storage full and zones were wide open. I'll check on it again, but guessing it will be out by noon.
time ..............bottom temp..........mid temp.............top temp
910pm................45f.......................45f....................48f
1040pm..............49.6.....................53.4...................73.4
1135pm..............50.5.....................65.1...................98f
1240am..............54.5.....................84.7...................127.9
140am................63.1.....................108.5..................148.6
330am.................79.7....................130.1..................160.7
355am.................84.4....................134.8..................162.7
Than a short nap
7am...................119.5....................158.....................172.4
915am................136.4.....................167.9.................177.8
945a...................141.8.....................171.1.................179.6
I have a 1800 sq/ft 2 story house, built about 12 yrs ago. Standard insulation. Located on a hill and we had -18 below with about 7 to 10 mph wind. Shut down heating zones( 2 zones) in house while wiring in BLT control and other related equipment. Probably had house offline for about 2 hours, from about 11pm to 130am. Once turned back on, zones called for heat all the time, while heating the storage. Also I located my boiler in an unattached garage aprox 40ft away, had a total run of 40ft underground and 60ft in buildings. Don't have all my notes with me, but I filled it at various times, not full each time, but I probably filled it complete about 4 times? I filled it last about 7am this morning, put too much wood in,fan shut down a couple of times, storage full and zones were wide open. I'll check on it again, but guessing it will be out by noon.
time ..............bottom temp..........mid temp.............top temp
910pm................45f.......................45f....................48f
1040pm..............49.6.....................53.4...................73.4
1135pm..............50.5.....................65.1...................98f
1240am..............54.5.....................84.7...................127.9
140am................63.1.....................108.5..................148.6
330am.................79.7....................130.1..................160.7
355am.................84.4....................134.8..................162.7
Than a short nap
7am...................119.5....................158.....................172.4
915am................136.4.....................167.9.................177.8
945a...................141.8.....................171.1.................179.6