Now I can read it. My eyes are fine, but my head hurts
I've seen this setup before, and I can't figure out what's happening in this diagram. I've puzzled 'till my puzzler is sore.
Let's say for the sake of the argument that all the circs are the same size, and to make life simple, the indirect and its circ are gone.
Let's say that the EKO is active and its circ is putting out 10gpm at 180 degrees, and that the zones create a 20 degree drop.
There's a circ between the EKO and the oil boiler, so I'll assume that there's no flow into storage from the EKO at this point. The Oil boiler has another circ on the return from the zones - perhaps we can assume 10gpm for that as well, lacking any other data. That would put 20gpm through the oil boiler - half hot water from the EKO, and half cold water from the zones.
That means that water coming out of the oil boiler is halfway between the outlet temp of the EKO and the return temp from the zones, and 20 degrees above the zone return temp.
That means the oil boiler outlet would have to be 160, and the zone return would have to be 140. That 20gpm at 160 degrees would then split - 10 to the zones, and 10 back to the EKO via the bottom of storage.
In this scenario, you're only running your zones at 160 - I just don't get it. Am I missing something?
This problem gets even worse running off storage, where your starting temperature is lower and your really want to be returning the coldest possible water to storage.