![Hydraulic Separator Storage, delta T boiler Circ, delta P load C Hydraulic Separator Storage, delta T boiler Circ, delta P load C](https://www.hearth.com/talk/data/attachments/83/83138-a9be5be8cf16b92357b1ac179db530e3.jpg)
It has been a while (again). The design I have attached is my final stab at making things as simple and efficient as possible and I will be ordering parts as soon as this thread has run its course. The boiler room has been invaluable to me so I have included a lot of info in hopes that this post might be useful to those taking their first look around. If this is all old hat my apologies to you for the lack of brevity. Do your worst.
Diagram Legend.
A. 007 Taco Delta T Circ http://www.pexsupply.com/Taco-007-VDTF5-007-Variable-Speed-Delta-T-Cast-Iron-Circulator-Pump-115V sized with http://www.taco-hvac.com/uploads/FileLibrary/SelectingCirculators.pdf
B. Danfoss Mixing Valve
C. Watts Air Separator http://www.pexsupply.com/Watts-0858548-1-1-4-AS-MB-Microbubble-Air-Seperator
D. 86 GalPressure Tank http://www.pexsupply.com/Amtrol-150N32-THERM-X-TROL-ST-210V-Expansion-Tank-86-Gallon-Volume
sized with http://s3.pexsupply.com/manuals/1260456456055/20376_PROD_FILE.pdf
E. Storage – 2 horizontal 500 gal. tanks welded to be hydraulic seperators
F. Grundfos Delta P Circ http://www.pexsupply.com/Grundfos-59896832-ALPHA-15-55-F-LC-Cast-Iron-Circulator-Pump
G. Mixing Vavle for Radiators http://www.pexsupply.com/Taco-5004-C2-1-Sweat-5004-Mixing-Valve-3653000-p
H. Mixing valve for Radiant Floor http://www.pexsupply.com/Taco-5004-C2-1-Sweat-5004-Mixing-Valve-3653000-p
I. DHW Circ - not sure what to use here-- any thoughts on something cheap? 1 GPM and 1.5ft head
J. BioMass 40
K. Taco Zone Sentry Valves http://www.pexsupply.com/Taco-Z075T2-1-3-4-Zone-Sentry-Valve-Threaded
L.Watts 125 psi relief valve http://www.pexsupply.com/Watts-0156481-3-4-40XL-5-TP-Relief-Valve-125-psi-12821000-p
Questions
1. Control suggestions for the DHW circ?
2. Should their be an air separator or float vent at the top of storage.
3. Is the air separator/expansion tank location ideal?
4. I want to use a Grundfos Alpha as my load circ but I am not sure how its control works and how it would "see" the different heads and flows of the radiant and radiator zones. Here is the specs as well as I am able to calculate:
-10 loops radiant - these are serving a 40000btu/hour load so the max flow per loop is .4 gpm but The taco circa sizer (http://www.taco-hvac.com/uploads/FileLibrary/SelectingCirculators.pdf) says that minimum flow in 1/2" pex should be 1.2 gal per minute. At this flow the max head is 16.56 ft. The loops are grouped in to 3 zones
1 of 5 loops - 2 or 6 GPM
1 of 3 loops - 1.2 or 3.6 GPM
1 of 2 loops - .8 or 2.4 GPM
- 4 Zones of Radiators all having flow below 2 gpm and head below 2 ft.
How will the ALPHA ensure enough flow in the different zones based on pressure changes. Is it big enough in general? Here is its pump curve- http://www.pexuniverse.com/sites/default/files/imagecache/product_full/aplha%20perf_c.jpg
5. I know my tanks have some scale in them. Do I need a sediment filter?
6. Total system size is roughly 1140Gal - 1000 gal storage, 40 gal boiler, 100gal for everything else. The THERM-X-TROL ST-210V Expansion Tank (86 Gallon Volume) has a capacitance of 46.44 gal. I calculated using http://s3.pexsupply.com/manuals/1260456456055/20376_PROD_FILE.pdf a requirement of 41 gal. Does this seem right?
7.How does one size load mixing valves? do I need 3/4" or 1".
8. Where should I have isolation valves, check valves, drain valves, fill valves and other basic fittings.
9. Controller ideas to turn on the electric boiler only if there is a call for heat from a zone and the temp in the tanks is below a certain point?
10. Is delta 35 deg F a good assumption for radiators?
11. Water treatment suggestions?
12. Any and all thoughts, suggestions, critiques or comments would be appreciated. I bought my BioMass and had my tanks made 3 years ago this past fall based on readings here in the boiler room and it is relieving and exciting that i finally have the time, budget and brain space to get this system up and running. What a strange and wonderful journey.
Thanks
Augie