I grew up using the HS Tarm Solo burning wood since 1980 and install the same model in my new home in 2002, an HS Tarm Solo MKII. My brother lives in my parents home now and continues to uses the original HS Tarm to heat the home. Both have an oil boiler that we use in the warmer months for hot water and back up heat if needed.
We actually keep the oil boiler turned off all winter unless we will be away from the home for a long time.
Each home is just over 5000 SQ FT and I heat my garage and basement with a Modine units.
We live in norther NH where outside temps with winds can go below - 50 degrees. My HS Tarm solo has run perfectly using wood or coal since installed.
Recently the outside temps have gone below zero. HS Tarm water temperature is continuing to increase to 210 degrees when all 6 zone circulators are running as all thermostats are calling for heat.
BEFORE ANY ONE SUGGEST CHECKING THE TARMS IN LINE CIRCULATOR, I'VE ALREADY DONE THIS AND REPLACED WITH A BRAND NEW ONE.
All valves are open and working correctly.
I've also purged the entire system, running new water through each zone, making sure there's no air locks. Plus, there are are air releive vales all over the place too.
The plumbing for the system is set up correctly for a home using both oil and the HS Tarm. The diagram was followed perfectly. when we turn off the oil, it's only the burner, so all other controls are in place and functioning.
What I have found is when all 6 zones are running, the return lines are entering the 2 inch main in front of the hot water coming from the Tarm boiler. The water is merging with the hot water coming from the HS Tarm and being diluted down to 120 degrees.
This is causing all the water being pumped through all zones to only be at 120 degrees!
The circulator pump pushing the water through the Tarm is a Grundfos multo speed, which has at least twice the power as the TACO pumps moving water throughout the house. Again, I've never had this problem in the past.
Attached are pictures of the boilers and plumbing.
Does anyone have any thoughts>
We actually keep the oil boiler turned off all winter unless we will be away from the home for a long time.
Each home is just over 5000 SQ FT and I heat my garage and basement with a Modine units.
We live in norther NH where outside temps with winds can go below - 50 degrees. My HS Tarm solo has run perfectly using wood or coal since installed.
Recently the outside temps have gone below zero. HS Tarm water temperature is continuing to increase to 210 degrees when all 6 zone circulators are running as all thermostats are calling for heat.
BEFORE ANY ONE SUGGEST CHECKING THE TARMS IN LINE CIRCULATOR, I'VE ALREADY DONE THIS AND REPLACED WITH A BRAND NEW ONE.
All valves are open and working correctly.
I've also purged the entire system, running new water through each zone, making sure there's no air locks. Plus, there are are air releive vales all over the place too.
The plumbing for the system is set up correctly for a home using both oil and the HS Tarm. The diagram was followed perfectly. when we turn off the oil, it's only the burner, so all other controls are in place and functioning.
What I have found is when all 6 zones are running, the return lines are entering the 2 inch main in front of the hot water coming from the Tarm boiler. The water is merging with the hot water coming from the HS Tarm and being diluted down to 120 degrees.
This is causing all the water being pumped through all zones to only be at 120 degrees!
The circulator pump pushing the water through the Tarm is a Grundfos multo speed, which has at least twice the power as the TACO pumps moving water throughout the house. Again, I've never had this problem in the past.
Attached are pictures of the boilers and plumbing.
Does anyone have any thoughts>