I want to add a wood furnace to my existing furnace system. I live in Ohio. I have a 2500 square foot 2 story house with a full basement. It was built 10 years ago. Well insulated, double pane glass. What BTU rating do I need?
coppermouse said:I cannot really say as far as the previous gas usage as I have always used a wood stove to heat with.
No it does not heat water, it just has a heat exchanger built into the unit.
coppermouse said:I cannot really say as far as the previous gas usage as I have always used a wood stove to heat with.
No it does not heat water, it just has a heat exchanger built into the unit.
coppermouse said:That is correct I normally don't use the gas furnace except when traveling, then I turn it low (like 45)
I have lived in the house since I built it 10 years ago. I will have to check on the stove, it has been a long time, I think it is an Englander, and it has 4 (1 1/2") round pipes coming out the top front of it that a blower is attached to. There is a catalytic converter in it. Also I cut my own wood and it is difficult to quantify, maybe 4 cords or so, but that is just a quess.
castiron said:My home is a 1650 sq ft ranch built in 1950. It has 2x4 walls with blown-in fiberglass, is fairly air-tight, has double plane windows (no gas between them though) and used only about 147 CCF of NG last Dec and 100 CCF in Jan and in Feb. Since about 15 CCF is for hot water each month, Dec used about 132 CCF which means about 15,000 BTU/hr is required as heat input to the home after taking into account inefficiencies (furnace is 96% eff and 15% duct losses).
132 CCF/month x 100,000 BTU/CCF x 0.96 eff x 0.85 eff x month/30 days x day/24 hrs = 14,960 BTU/hr
In Jan and Feb it only used about 10,000 BTU/hr. So, if you run a wood stove or attached wood unit, the hourly input of heat into the home is small. Scaling up to your home, I'm guessing about 22,000 BTU/hr to heat the two main floors and more if you're heating the basement.
Remember though, the figures I quoted are for my home after taking into account MY inefficiencies. As Craig said, your existing unit may be less inefficient and the real heat input your house requires is lower than you think. That's why he suggested you look at prior bills and take into account furnace and duct losses. I think wood stoves are rated as heat OUTPUT (which means you only have to take into account duct losses and any air-to-air or air-to-water exchanger losses) so for you to get say, 30,000 BTU input to the home, your wood stove needs to output about 47,000 BTU/hr.
30,000 x (1/0.85 duct loss) x (1/0.9 exchange loss) = about 40,000 BTU/hr
I don't think max ratings run this low so it would seem that most any typical sized unit would work, but as Web said, start with your previous bill for a cold month and work it backwards taking into account the inefficiencies. If you want, tell us the month, the energy used (tell us if it includes energy for hot water) and tell us the type furnace and efficiency and we can get a ball park idea. I'm assuming this is a wood unit that heats water and circulates it through a heat exchanger installed in your heating ducts to then extract the heat. Is this correct?
karl said:I'm a bit confued Elk. Using your calculations, I need 60,000 btus to heat my house. The output on my furnace is 180,000. Yes it's an old furnace and it does heat the really well. I just can't see where you use the same numbers for a stove and a furnace. One cycles and the other doesn't. I can buy needing 60,000 continuous to heat this house to 70 on a 0 degree day, but I would hate to not have any excess left.
karl said:I understand. What is troubling me is that a furnace cycles more than a stove, so I would think a stove wouldn't need to be as big. Anyway, my Summit is oversized for the house according to Elk's numbers, so I won't have to worry about being cold. The big difference between me and most people on here is that I let the house cool off alot. I am out of town 3 or 4 days a week and set the thermostat on 50 when I'm gone. After a few days, not only is the air cold. The block is cold, the furniture is cold, etc. That's a huge amount of mass to bring up to temperature. With the gas furnace it cycles on and off alot to heat the house. It gets the air warm and turns off and then the furniture and walls suck the heat out of the air and it starts all over again. I'm hoping to use the Summit to bring the house up to temperature when I get home. That will save me tons on my gas bill.
karl said:I didn't say I had virtually no insulation. I have 2x6 walls that are insulated and about 12" in the attic. I have good windows. My only week place is the basement and crawl space.