Jebatty's thread about controlling the draft fan to keep flue temps from going inefficiently high makes me want to ask a question that is on my mind:
How low could you drive the flue temps (assuming that you are doing it by catching more BTUs in the boiler's heat exchanger) without negative consequences (condensing flue gas moisture in the boiler is obviously to be avoided, as is significant moisture build up in flue pipe and chimney)?
I was reading some literature on some commercial boiler retrofit turbulator manufacturers' web sites, along with some academic papers on turbulators (I embrace my inner nerd...), and the only specific figure that I found- for an oil boiler- was 265 at the boiler flue collar, plus an additional half degree farenheit for every foot of distance between the boiler and the final chimney outlet.
In my case, between flue pipe and chimney height, that would be 265 + 40 / 2 = 285 degrees (using the oil boiler formula) at the boiler flue collar- which is way lower than my boiler actually runs on flue gas temps, and way lower than I have heard people report from other makes and installations.
Interested in peoples' thoughts on this
How low could you drive the flue temps (assuming that you are doing it by catching more BTUs in the boiler's heat exchanger) without negative consequences (condensing flue gas moisture in the boiler is obviously to be avoided, as is significant moisture build up in flue pipe and chimney)?
I was reading some literature on some commercial boiler retrofit turbulator manufacturers' web sites, along with some academic papers on turbulators (I embrace my inner nerd...), and the only specific figure that I found- for an oil boiler- was 265 at the boiler flue collar, plus an additional half degree farenheit for every foot of distance between the boiler and the final chimney outlet.
In my case, between flue pipe and chimney height, that would be 265 + 40 / 2 = 285 degrees (using the oil boiler formula) at the boiler flue collar- which is way lower than my boiler actually runs on flue gas temps, and way lower than I have heard people report from other makes and installations.
Interested in peoples' thoughts on this