I have my system up and running but I'm having difficulty setting up my 3 way valve control.
Equipment on hand:
Valve - Honeywell Motorized Valve Linkage (0 to 10 volts)
Controller - Siemens RWD62U
Sensor - Siemens Immersion Temp Sensor Nickel 1000Ohm
I purchased the software to supposedly program the controller but I thought I could set it up from my desktop and take it to the boiler room but the controller does not remember what I programmed so I have to take the desktop to the boiler room.
What I want is the following:
No Power - Valve Closed(heated water straight to tanks for boiler protection in case of power outage).
Under 125 degrees Valve Open(10 volts) so water circulates back to boiler inlet.
Over 165 degrees Valve Closed(0 volts) so water goes to storage tanks.
In between 125 and 165 voltage varies to modulate valve so I don't get a rush of cold water to boiler from bottom of tanks.
I guess my question is has anyone had any experience using this style of controller in this application and how did you set up the parameters. Or is there a better way to change the voltage to the valve depending on water temp to modulate like I want it to?
Equipment on hand:
Valve - Honeywell Motorized Valve Linkage (0 to 10 volts)
Controller - Siemens RWD62U
Sensor - Siemens Immersion Temp Sensor Nickel 1000Ohm
I purchased the software to supposedly program the controller but I thought I could set it up from my desktop and take it to the boiler room but the controller does not remember what I programmed so I have to take the desktop to the boiler room.
What I want is the following:
No Power - Valve Closed(heated water straight to tanks for boiler protection in case of power outage).
Under 125 degrees Valve Open(10 volts) so water circulates back to boiler inlet.
Over 165 degrees Valve Closed(0 volts) so water goes to storage tanks.
In between 125 and 165 voltage varies to modulate valve so I don't get a rush of cold water to boiler from bottom of tanks.
I guess my question is has anyone had any experience using this style of controller in this application and how did you set up the parameters. Or is there a better way to change the voltage to the valve depending on water temp to modulate like I want it to?