Hello folks,
New member here, hailing from The Champlain Valley of Vermont.
I'm just completing the install of a Harmon PB105 boiler plumbed primary/secondary to 2 radiant floor zones, one baseboard zone, an indirect DHW tank (smart 50), and eventually the hot tub and shop.
So far I've had the Harmon fired up a few times connected only to the DHW tank to check things out, and chase leaks in the primary loop.
Ooohh that was fun! I love leaks!
Anyway, to my first question I came here for!
I have tested the draft on the install. I have approx. 13ft of rise in my Simpson PVP vent. I measured a high draft of 0.80 I.W.C.
The problem I have is that I can't get the low draft into the spec range that Harmon indicates in the manual.
With the adjustment pot turned all the way down, I still measure a low draft of 0.70 I.W.C.
The specs indicate that low draft should be between 0.25 and 0.35, with a max of 0.55.
Anyone have any experience with this issue?
Also, I need to "vent" about the performance of the Simpson PVP vent pipe... it leaks!! "No silicone required" my A***
Ok.
Thanks!
Nat
New member here, hailing from The Champlain Valley of Vermont.
I'm just completing the install of a Harmon PB105 boiler plumbed primary/secondary to 2 radiant floor zones, one baseboard zone, an indirect DHW tank (smart 50), and eventually the hot tub and shop.
So far I've had the Harmon fired up a few times connected only to the DHW tank to check things out, and chase leaks in the primary loop.
Ooohh that was fun! I love leaks!
Anyway, to my first question I came here for!
I have tested the draft on the install. I have approx. 13ft of rise in my Simpson PVP vent. I measured a high draft of 0.80 I.W.C.
The problem I have is that I can't get the low draft into the spec range that Harmon indicates in the manual.
With the adjustment pot turned all the way down, I still measure a low draft of 0.70 I.W.C.
The specs indicate that low draft should be between 0.25 and 0.35, with a max of 0.55.
Anyone have any experience with this issue?
Also, I need to "vent" about the performance of the Simpson PVP vent pipe... it leaks!! "No silicone required" my A***
Ok.
Thanks!
Nat