I'm working on a Hearthstone Tucson model 8720. The pilot light looks good, lights up fine and is hitting the thermopile and the thermocouple. I hold the pilot light button one for a full minute and a half. The pilot goes out as soon as I let off the button.
Following the troubleshooting guide for this model, I checked the voltage on the thermocouple: 23.6 mV. It only requires 15. I checked the thermopile voltage and got it up to 450 MV +. It says to check voltage between the valve body and solder connection on the rear of the valve, where the blue wire connects. It should be no less than 7 mV. I get 0 mV. Cause would be faulty connection. It attaches to a device, pictured in the second attachment (with two connections). The other wire was not plugged in to anything (third picture). I tried jumping the thermostat connections. I hear a click, but it does not change anything.
I changed the valve body out, and am getting the same results with all the tests. Reasonable to assume that the old one was fine. Next step it to change the thermocouple even though it tests out to spec. Would anyone have suggestions?
Following the troubleshooting guide for this model, I checked the voltage on the thermocouple: 23.6 mV. It only requires 15. I checked the thermopile voltage and got it up to 450 MV +. It says to check voltage between the valve body and solder connection on the rear of the valve, where the blue wire connects. It should be no less than 7 mV. I get 0 mV. Cause would be faulty connection. It attaches to a device, pictured in the second attachment (with two connections). The other wire was not plugged in to anything (third picture). I tried jumping the thermostat connections. I hear a click, but it does not change anything.
I changed the valve body out, and am getting the same results with all the tests. Reasonable to assume that the old one was fine. Next step it to change the thermocouple even though it tests out to spec. Would anyone have suggestions?