pharmer said:
My current setup is a zero-clearance fireplace with what I believe is a fully lined chimney. My question is how much would it involve to replace the fireplace with the insert? Does the chimney lining have to be replaced? Is this a job I could consider perfoming on my own?
Page 13 of the owners manual states the following:
Zero Clearance Fireplace Requirements
These are factory bulit insulated metal fireplaces
that are usually framed into the wall with lumber. The
term, "Zero Clearance" refers to the fact that wood framing
material can be in contact with the outer shell of the
unit.
1. The chimney must be at least 15 feet high but not
more than 33 feet high.
2. The chimney must have a stainless steel liner.
3. The entire fireplace and chimney must be clean and
in good condition. Any damage must be repaired
before installing the insert.
4. The fireplace and chimney must meet local building
codes.
5. Must line chimney all the way to the top.
6. The smoke shelf, internal baffles, damper and glass
or metal doors may be removed as necessary.
7. Internal parts such as refractory linings (firebricks),
insulation, firebox walls or door frames may not be
removed or altered.
Zero Clearance Fireplace Installation
The first step is to take careful measurements to be
sure the insert will fit into fireplace. It is required that
zero clearance installations be lined to the top of the chimney.
The liner can be rigid or flexible with a chimney cap
and top sealing plate installed. The liner should be stainless
steel and listed to UL-1777.
Chimney Liner
(broken link removed to http://www.harmanstoves.com/doc/exceptioninsertm.pdf)