Started the boiler today after the summer shutdown and getting a "Combustion air supply faulty or blocked" at end of the preparation phase.
Spent hours checking values and cleaning inside the boiler, air intakes and the flue. Have also recalibrated the Lambda probe which is only 12 months old after having failed during last summers shutdown (lessons learnt...don't turn these boilers off for an extended period)
Does anyone have any suggestions? I'd rather replace a failed part based on an incorrect status value rather than just swapping parts in hope. Previously the Lamdba probe error messages was a clear "Sensor element of the broadband probe faulty"
From what I understand the boiler only has 2 sensors, Lambda and flue temperate, so I'm assuming its using the Lambda to measure the oxygen.
Current values below which seem to be relevant. I haven't changed any values, but just not sure what value the preparation phase is monitoring for before throwing the error
Paul
Spent hours checking values and cleaning inside the boiler, air intakes and the flue. Have also recalibrated the Lambda probe which is only 12 months old after having failed during last summers shutdown (lessons learnt...don't turn these boilers off for an extended period)
Does anyone have any suggestions? I'd rather replace a failed part based on an incorrect status value rather than just swapping parts in hope. Previously the Lamdba probe error messages was a clear "Sensor element of the broadband probe faulty"
From what I understand the boiler only has 2 sensors, Lambda and flue temperate, so I'm assuming its using the Lambda to measure the oxygen.
Current values below which seem to be relevant. I haven't changed any values, but just not sure what value the preparation phase is monitoring for before throwing the error
- Residual Oxygen content - Usually around 21% during preparation
- Oxygen Control 35%
- Residual Oxygen content setpoint 9%
- O2 Controller max 120%
Paul