Flat plate HX question.

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.
  • Super Cedar firestarters 30% discount Use code Hearth2024 Click here
Status
Not open for further replies.

maple1

Minister of Fire
Sep 15, 2011
11,083
Nova Scotia
Kind of general, but basically - what is the point of diminishing return when heating just DHW with a flat plate, as far as how big of a hx? (Number of plates)

Looking at 5x12, wondering if 10 plates will do, or if I should bump up to 20. Looking to get a good close approach, and send the return back to storage as cool as I can. I've got an Alpha on the supply side, and a B&G Ecocirc ready to plumb in on the DHW side - so I can vary my flow on both sides fairly good.
 
Here's some ball-park/sanity-check numbers.

An electric household DHW supplies 4500 watt or about 15000 btu / hour.

Below is part of a table for a 5x12-10 HX I found:
Code:
OKO Brazed 5x12-10

hot side 180 degF => 160 degF
cold side 40 degF => 140 degF

btu/h  hot cold
       gpm  gpm
25000  2.6  0.5
40000  4.1  0.8
50000  5.2  1.0
Back when I got my thermodynamics merit badge I might have been able to calculate what the flows and deltaTs would be, but all I can offer today is guesswork. Looks like for a 5x12-10 at 15000 btu / hour you might be able to get 180 => 140 on the hot side and 55 => 140 on the cold side, with a couple gpm on the hot side and less than a gpm on the cold side.

[Edit:] This all assumes you'd be using the HX to charge a DHW storage tank or conventional electric DHW tank. On demand is a whole different problem.
 
Last edited:
Here's some ball-park/sanity-check numbers.

An electric household DHW supplies 4500 watt or about 15000 btu / hour.

Below is part of a table for a 5x12-10 HX I found:
Code:
OKO Brazed 5x12-10

hot side 180 degF => 160 degF
cold side 40 degF => 140 degF

btu/h  hot cold
       gpm  gpm
25000  2.6  0.5
40000  4.1  0.8
50000  5.2  1.0
Back when I got my thermodynamics merit badge I might have been able to calculate what the flows and deltaTs would be, but all I can offer today is guesswork. Looks like for a 5x12-10 at 15000 btu / hour you might be able to get 180 => 140 on the hot side and 55 => 140 on the cold side, with a couple gpm on the hot side and less than a gpm on the cold side.
 
How many GPM do you want to transfer. I started with a 5X10- 30 on my solar storage/ DHW HX. With well water at 55F I could provide a endless shower, about 1.5 gpm with the solar tank as low as 120F.

I now have a 3X8-40 and when the solar tank drops to 130 I have to flow back the shower gpm to keep the shower temperature warm enough.

If budget allows more plates = more performance, keeping in mind domestic water conditions will tend to foul the plates and limit transfer as you use the system.

Some good HX sizing info starting on page 34 of this journal. The example shows a 5X12 -30 With 130F on the "A" side, 120F "b" side 50F incoming supply, 5 gpm flow rate.

http://www.caleffi.us/en_US/caleffi/Details/Magazines/pdf/idronics_11_us.pdf
 
I'll d/l that file & read through it later when I have more time - thanks very much.

Asking as I want to be able to preserve stratification & draw down my storage as much as possible, when recharging an 80 gallon electric heater from storage only. GPMs are pretty loose - I can dial each side to some extent & demand doesn't really factor in with a tank that big & intermittent water usage.

I had pretty well decided to go with a 20 over a 10, but had no info to base that on, just a hunch. But then also got to wondering if it would gain me much by going even bigger.
 
Look at the tables. Relevant are Side A in and out and Side B in and out, gpm, pressure drop Sides A and B. Then pick circulators that will move the desired gpm at the specified pressure drop. Remember that 1 psi = 2.34 feet of pump head. For dhw, issues also will include minerals in the water and scale build-up in the hx. Provide for shut-offs and unions on the hx to so that it can be removed and flushed to clean scale as needed. And likely a mixing valve on the side feeding the house to keep water temp at about 125F maximum, although dishwashers need or can use hotter water.
 