Many thanks to all who contribute so much to this forum - you have allowed me to take what I first thought was a pie-in-the-sky idea and make it reality.
I was able to fill the system with air friday and pressure test. I found about a dozen leaks in the near boiler piping. Some observations for those in process now:
1. Danfoss Valve ports are not tapered to NPT female specs. All three ports leaked badly, and I had to disassemble the entire near boiler pipe loop to fix the leaks. I used pipe dope only initially-not enough to seal on this fitting. I reassembled using pipe dope, good teflon tape, and more pipe dope.
2. The 2" inlet and outlet on the EKO are not standard NPT either. Repeat above on those joints.
3. Chinese 1.25" fittings don't mate well with nipples from Taiwan. All of the 2" nipples I bought were made in Taiwan, and they all leaked when threaded into Chinese or Thai cast fittings. All of the other nipple sizes and straight pipes were either Chinese or locally made and had no leaks. I had to use Teflon tape on these fittings as well.
4. I have yet to find a copper-to-copper union that does not leak. I was unable to get all brass in 1", and I am facing a big repair where I installed two of the copper unions. Does anyone have any way to seal these unions that doesn't involve removing them?
5. No one on this forum mentioned how bad black pipe smells the first time it is heated to 185*. I was unprepared for this and got an earful from the wife.
6. I spent the last three days getting the air out of the system. I received boiler prep and treatment solutions from Dave at Cozy Heat, but I am hesitant to drain/fill the system because of the time involved in removing air again. Thoughts on whether I should use the chemicals?
7. After firing the EKO for the first time, the boiler room filled with not so much smoke as a haze - there was a smoke smell, but I could not see anywhere it was coming from. The pipe smell was there as well. Is there a burn-in/burn-off for this unit that could cause the haze?
Operational observationsto follow, but so far the system looks good.
I was able to fill the system with air friday and pressure test. I found about a dozen leaks in the near boiler piping. Some observations for those in process now:
1. Danfoss Valve ports are not tapered to NPT female specs. All three ports leaked badly, and I had to disassemble the entire near boiler pipe loop to fix the leaks. I used pipe dope only initially-not enough to seal on this fitting. I reassembled using pipe dope, good teflon tape, and more pipe dope.
2. The 2" inlet and outlet on the EKO are not standard NPT either. Repeat above on those joints.
3. Chinese 1.25" fittings don't mate well with nipples from Taiwan. All of the 2" nipples I bought were made in Taiwan, and they all leaked when threaded into Chinese or Thai cast fittings. All of the other nipple sizes and straight pipes were either Chinese or locally made and had no leaks. I had to use Teflon tape on these fittings as well.
4. I have yet to find a copper-to-copper union that does not leak. I was unable to get all brass in 1", and I am facing a big repair where I installed two of the copper unions. Does anyone have any way to seal these unions that doesn't involve removing them?
5. No one on this forum mentioned how bad black pipe smells the first time it is heated to 185*. I was unprepared for this and got an earful from the wife.
6. I spent the last three days getting the air out of the system. I received boiler prep and treatment solutions from Dave at Cozy Heat, but I am hesitant to drain/fill the system because of the time involved in removing air again. Thoughts on whether I should use the chemicals?
7. After firing the EKO for the first time, the boiler room filled with not so much smoke as a haze - there was a smoke smell, but I could not see anywhere it was coming from. The pipe smell was there as well. Is there a burn-in/burn-off for this unit that could cause the haze?
Operational observationsto follow, but so far the system looks good.