I'm building a hearth and surround for a free standing wood stove. I went with .25" durock on studs 16" O.C. and plan on cutting durock furring stacked and fastened on the studs as spacers for the 1" air gap, then topping with .5" durock, and finally 1-2" thick natural slate on the face (we live near a slate quarry).
The issue I am having is that the total width of the .5" durock and furring (providing the 1" air gap), and the 1/4" durock under that is 1.75". With 2.25" screws I'm only going to have .5" of penetration. Manufacturer's specifications call for minimum .75" penetration at 8" spacing for walls (6" for ceilings). I suspect those specifications are also intended for a tile face and not a heavier stone.
My plan is to space the 2.25" screws at 4", and I'm considering adding in some 3" deck screws every 12".
Does anyone see any issues with this or have a better solution?
Will the 4" spacing be sufficient or should I include the deck screws?
The issue I am having is that the total width of the .5" durock and furring (providing the 1" air gap), and the 1/4" durock under that is 1.75". With 2.25" screws I'm only going to have .5" of penetration. Manufacturer's specifications call for minimum .75" penetration at 8" spacing for walls (6" for ceilings). I suspect those specifications are also intended for a tile face and not a heavier stone.
My plan is to space the 2.25" screws at 4", and I'm considering adding in some 3" deck screws every 12".
Does anyone see any issues with this or have a better solution?
Will the 4" spacing be sufficient or should I include the deck screws?