Close to the first burn...that said, miles from the finish line!
rvtgr8
I have it all piped in and ready to go, but I am still without an adequate control strategy. I originally purchased a Tekmar 356 for use on a on a mixing valve. I no longer am utilizing the mix valve idea and it does not appear that I can use the 356 in my control scheme. If I am wrong I would appreciate a heads up. If I am right, I will let it go at a bargain. My problem is not unique. I want my Garn to be the main heat source unless for some reason the temperature in its water supply drops below a certain point. In that case, if I get a heat call from the system, I want the propane ($$$$$) boiler to become the main source until I get the Garn heated back up to a useful temperature range.
I have seen some members using off-the-shelf controls. Unfortunately for me, most of those controls are in the $600 + range, well beyond my fiscal reach.
I have seen some members build their own control systems. While they have impressed me with their resourcefulness, intelligence, and frugality, these members must have to shell out a fortune to modify the doors in their homes so they can get their giant brains from room to room. My doors appear to need no modification at this point.
I am nearing the end of my money allotted for my project and cannot afford to hire a HVAC engineer to help me over this last hurdle. So, I need advice. Can anyone point me in the right direction on some literature for me to build my own? Can anyone figure a way for me to modify the uses of the Tekmar 356 to suit my purposes? Can someone help me figure a way to develop a manual switchover so I can use the system until I can afford a more expensive solution?
i'm no einstein but i would put the heat exchanger on the cold return to the boiler. that way you heat your boiler first so it will only fire when it gets cold water flowing in.
Foolish to heat the Burnham boiler with the garn, but this has already been covered.
As far as controls:
Does the Burnham stay hot all the time or only run on call for heat?
Is there a control system in place for the Burnham now?
Is there a free set of contacts on the Garn that open on rise above set temp you can use to kill power to the Burnham?
Does the Garn even come with any control for pumps or is it all up to you.?
These will help determine which route to take.
One of the more simple routes would be to use an aquastat on the garn to throw a relay/relays to hand off control to the Burnham when the Garn is to cool
to use. If you just want emergency backup treat them as two separate systems with separate thermostats and set the Burnham TT well below the Garn so
it will only come on if the house gets cold. Downside to this is the boiler may stay hot anyway depending on the type of existing setup.
Work backwards from your house thermostat, TT controls zone valves, zonevalves control the BH or heat exchanger pump(depending on mode oil or wood) and
if heat exchanger pump then also control the pump on input side of exchanger. Wood to oil mode could use a relay kill power to BH, another relay to switch from BH
pump to flate plate pump.
I am not familiar with the Garn or it's controls but this is not that difficult if you work through what needs to run and when. There is a recent thread on relays
and there applications, check it out if you are not familiar.
Kris
The controls for the Burnham are pretty simple and straight forward. The thermostats call for heat and the Burnham opens its flue vent and starts the burn. I will draw up the schematic and send it later this evening. Thanks Kris.
my asumption was that the boiler was always on so it is always at a constant temp. so runing thru it first it will not run until no heat comes out of the garn. you would not be wasting any thing and the controls would be alot eas.ier
Use the same controls, just have the injection pump turn on also.
Tim
EK, I am sorry I did not respond earlier. I was busy watching the Steelers pound my Broncos into a bloody pulp. Am I correct in saying that that your last comment was the reasoning behind your earlier suggestion of having the HX on the cold return? My concern there is that my high mass loops running in the concrete create a pretty significant lag time before coming up to temp. I may not quite understand your point, but I appreciate your feedback.
Kris, I hope the control schematic was helpful. I like your suggestion and am flow charting your suggestion in the morning.
Tim, are you thinking that the controls within the Burnham are sufficient to control both boilers? I am curious about your reasoning, could you share a little more?
Robert
PS - Thanks you guys.
The key question is what does the BH do when it does NOT have a call for heat? Does it stay turned off and cold? Does it try to cycle periodically to keep it's water hot?
Assuming that it stays turned off and cold, then there are essentially two control strategies to control the three relevant pumps.
Pumps -
P1 - pump on Garn side of HX, should run when house calls for heat, and Garn is hot enough
P2 - pump on house side of HX, should run when house calls for heat, and Garn is hot enough
P3 - pump on Burnham, should run when house calls for heat, and Garn is NOT hot enough
Strategies -
1. Have two thermostats - T1 & T2. T1 is wired to turn on P1 & P2, and set for desired house temp. Put aquastat (or other sensor) on Garn side HX supply pipe, wired to interrupt T1 signal (thus keeping P1 & P2 from running) T2 is wired to Burnham thermostat inputs, and set to approx 5* or more LESS than T1. P3 is wired to Burnham pump control outputs
Method - If Garn is hot, T1 turns P1 & P2 on and off as needed to meet house demand. If Garn supply water drops below minimum required, aquastat prevents T1 signal from reaching pumps. House gets colder, until T2 turns on Burnham, which runs P3 as needed for heat - Wife gets cold & grumpy, sends rvtgr8 out to build fire in Garn... :coolsmirk:
2. One thermostat, set for desired temp. Aquastat or other sensor on Garn side HX supply pipe, wired to coil of DPDT relay. Thermostat wired to common terminals of relay. NC set of relay contacts wired to Burnham thermostat inputs, NO set wired to P1/P2 control. P3 wired to Burnham circ control.
Method - If Garn is hot, sensor closes, tripping relay, thermostat signals go through NO contacts to control for P1 & P2, turning them on and off as needed. If Garn cools down (or there is a failure in the sensor circuit, I wired this way as a fail-safe) the relay returns to off state, sending thermostat signal to Burnham, which again controls P3... Note that some signal may be appropriate to alert house that they are now running off the BH instead of the Garn, as both will be trying to maintain the same temperature setting.
The control logic for P1 & P2 can be very simple, just a relay or two as needed to turn the thermostat signal into on / off switching of the supply for the circs.
One can get much fancier, and spend a lot more money and effort, but IMHO the two approaches above are both workable, simple, and probably the cheapest way to go...
Gooserider
Goose has a good handle on the situation.
I like option #2, option #1 may be a problem because i THINK there are zone valves involved here. If so the TT signal to the Burnham probably comes
from the zone valves so the second thermostat would be tricky.
So.....think in terms of a complete separate system for the Garn. on a call for heat(from the zone valves?) you want to run the pumps on each side of the
flat plate. Like Goose said, insert DPDT relay in the thermostat line to the BH control, and from normally open contacts to the Garn side pump relay. Then all
you need is a signal to control the relay. could be line voltage or low voltage, depends on whats on the garn. If you hook it like goose suggested you will need
contacts on the Garn that CLOSE on temp rise. When the Garn heats up contacts close and energize relay, sending TT signal to Garn side pumps.
You will need some type of relay(24VAC coil?) for the garn side pumps, the thermostat signal will close this relay and run both pumps.
You may want a relay to kill power to Burnham boiler so it does not stay hot all the time, if it only fires on a call for heat it will NOT be needed.
If none of this makes any sense I may have to break out the kids crayons a make a schematic.
As far as football I'm a Ravens fan so I didn't care who won as long as the Steelers lost. Bummer... :down:
Edit: Remember the wiring is the easy part as long as you TURN OFF THE POWER, you don't get wet when you mess this up. Just don't let the smoke out
of anything, It's a bi%@$ to get back in.