Just looking for a second opinion and some insight. This winter was my first with an owb. Everything worked great. But now I’m finishing my shop and will be adding a second loop to it. My main concern is I think my pump is oversized for my house. So if that’s the case I’d use the 0011 for the shop and get the correct size for the house.
My boiler is 35’ from the house. Inside it’s 25’ to the boiler room. I have a total of 70’ of 32mm pex (1.25”) and 50’ of 1” pex. About 15 1” pex 90s, 8 full port ball valves, a 20 plate and a 30 plate heat exchanger.
Using Tacos TD10 I’m at around 9 feet of head.
My heat loss for my house is about 40,000 btu on design day. I shot for 50,000btu with a 20 degree drop which gave me 5gpm.
According to the curve for a taco 0011 at 9’ head it’s moving 23 gpm roughly. Is it necessary to move that much water.
Curious on what anyone else thinks. I’ve done enough number crunching the last few nights my brain is fried. Thanks.