Breckwell Big E installation - Vent pipe clearances with Pelletvent/Pelletvent Pro

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.
  • Super Cedar firestarters 30% discount Use code Hearth2024 Click here
Status
Not open for further replies.

ship_reck

Member
Hearth Supporter
Jan 30, 2008
40
Central MA
I have a general question regarding exhaust pipe clearances for an install of a Breckwell Big E. The owner's manual states 3" inch pipe clearance from combustible materials, which coincides with Simpson's Pelletvent pipe literature. But Simpson also offers Pelletvent Pro, which is UL listed for 1" clearance to combustibles.

Could I go with the Pelletvent Pro, and be closer than the Breckwell manual requires?

Thanks-
Tim
 
What does your Breckwell Dealer tell you. That is the first place to start.

The Breckwell manual is somewhat dated. Dura Vent Pellet Vent Pro only needs a 1" clearance to combustibles.

1.) Keep the clearances of the stove first.
2.) Keep your clearance for the pipe second.

When in doubt call Breckwell's Tech. line after you ask your dealer.

Eric
 
Status
Not open for further replies.