Boiler Tuning for Hot water coil.....

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.
  • Super Cedar firestarters 30% discount Use code Hearth2024 Click here
Status
Not open for further replies.

thebenchmaker

New Member
Hearth Supporter
I have a Smith Oil Burner with coil used for heating hot water. I keep my high at 160 and my low at 140. I have a mixing valve set at 140 its highest setting.
When I turn on my shower the hot water runs out fairly quickly, as boiler temp falls to 140, and then takes awhile to get hot again as the boiler returns to 160. If my shower is hotwater at 120, and the boiler never actually falls below this temp, what can I do to tune this issue. My diff, whatever that is is set to 20.


Thanks

ryan
 
I would suspect a mineralized coil. you can start out with exceedingly hot water(160/180) the mixing valve will temper it to the your setting on the mixing valve but then the water going through the coil is cold and can't absorb the heat fast enough The mixing valve can only mix if its getting hotter water imputed then its set for When the boiler cools down to the lower setting the boiler fires and runs to the hightemp limit at this point the cold water going thru the coil can absorb more of the heat it is exposed to. I would look into boiling the coil out with acid, or replacing the entire coil.
 
Thanks for response Plumbit.....
is there a relatively easy way to check coil,
and is it possible that the coil just can not keep up....?
but I think that it can because after the water cools and reheats out of the tap there is plenty of hot water......
 
I think you'll find with tankless coil setups you need the hotter boiler water to keep up with demand at times. An indirect setup gives you a buffer so you can be a little lower in temp. Put your boiler temp back up to 180-160 deg. Consider an outdoor reset control and a hot water priority control set up. At the least, if your boiler is a higher mass, try an intellidyne or beckett heat manger. They allow the boiler to fire to 180 deg but will let it float down to 140 depending on the demand.

Unless your hot water temp has fallen off over time acid cleaning probably won't help.

Mike
 
thanks mike, i will look into a beckett, what do you mean by mass? and as i understand, the diff dial sets a drift too correct? i have mine at 15 but it was at 10, does this actually work against me when i raise it?
 
benchmaker said:
thanks mike, i will look into a beckett, what do you mean by mass? and as i understand, the diff dial sets a drift too correct? i have mine at 15 but it was at 10, does this actually work against me when i raise it?

The becket model is a "budget" type version of the Intellidyne heat manager that is actually made for becket by them. Basically it "learns " your heat demand with sensors and will hold off or activate the burner depending on the rate of change of the demand. Typically it will go into the "economizing" mode and hold off firing the burner if there seems to be enough residual heat in the boiler to satisfy the demand thereby minimizing burner cycles thus saving money. That's the idea anyway. It will start the burner at about 140 deg decreasing. The burner needs to have a shut off point of 180 plus deg rising. I use an Intellidyne with a cold start with indirect water heater using one sensor. A tankless coil setup would use an additional sensor. I understand the heat manger is most effective with a boiler with higher mass, i.e., more gallons the better, and low mass heat loads such as as baseboard radiators.

Mike
 