Okay, I've been playing with 6" versus 8" chimney calculations, and have some results for comment, sanity checking, and general ridicule. ;-)
I Googled up this chimney calculator, which is pretty fun to fool around with:
http://www.engineeringtoolbox.com/natural-draught-ventilation-d_122.html?v=14&units=feet#
The part I played with is the "Natural Draft Air Flow and Velocity Calculator" about halfway down the page.
It's in metric, so to use it you have to convert units using the widgets on the left side of the screen, and know that for circular pipes, the "duct hydraulic diameter (m)" is the chimney diameter.
Once I waded through that, the fun began.
I set the interior temp at 68*, outside temp at 20*, and varied chimney diameter and height, in the following format:
Each line shows the chimneyheight/houseTemperature/OutsideTemperature/ and the resulting DraftPressure/AirFlow:
height/dia/insidetemp,F/outsideTemp,F/DraftPressure,N/m^2/flow,ft^3/min
14/8"/68/20/5.2(0.02water")/164
14/6"/68/20/5.2(0.02water")/88
24/6"/68/20/7.3(?water")/103
I found those results kind of interesting.
First, it seems the Draft pressure--the initial
draw on the stove--
depends on height and temperature only. But the resulting flow also depends on diameter, which determines the chimney's resistance to flow. This seems to say that, for a given temperature difference and chimney height,
a 6" pipe initially draws as hard as an 8" pipe, but has lower maximum flow , which all seems to make sense to me. (Of course this ignores bends, single/double wall stovepipe factors, which add their separate effects.)
Comments? Laughter?
You can also see from the two 6" diameter cases, that a taller chimney increases draw significantly, but flow not as much, as the pipe's resistance gets in the way.
I'm thinking this has implications for the Blaze King King too. The King and the Princess have almost the same maximum BTU output, with the biggest difference between the two stoves being a bigger firebox for longer burns. As one member pointed out, air demand is determined by burn rate, not firebox size, so the steady state air requirements for the Princess and King should be nearly identical, making a 6" pipe fine for the King under most conditions.
Right?
The only scenario I can think of where the King and Princess significantly differ would be reloading a hot firebox. Then the King's bigger load of fresh wood might outgas more, and briefly require more air to run the catalyst efficiently and pass EPA. I also note that the King's owner's manual (in the Definitions section under Chimney) says "Never use a chimney connector or chimney flue small than the stove exhaust,
unless approved by your local inspector." So an 8" chimney is not a hard and fast rule, but Blaze King doesn't want responsibility for anything smaller.
The two factoids together make me wonder if the reason the King specifies a bigger flue than the Princess with the same output, is to meet EPA emissions standards during hot reload.
Comments? Tomatoes?
One more interesting item. In Definitions under Draft, the BKK manual says it will smoke, burn poorly, and start hard with a draft less than 0.02" of water. According to my calculations ( ;-P ) that is the draft for a 14' high ideal chimney with a 50 degree temperature differential.
All this is of course inconclusive, and I could be completely wrong, but does makes me confident enough to risk installing the 24' high 6" diameter chimney (8" diameter double wall stovepipe up to the thimble) that I have on hand. What I'll do is frame the surface penetrations large enough for an 8" chimney install, making swapping one in relatively painless, if it comes to that.
Comments? lol
Well, there's my geeking out for today. I hope you found it useful and/or amusing.
George