twitch said:
If this seems a little far fetched, are there others here that have the same type of existing forced air setup that are using a boiler?
not far fetched at all; I am building something similar where I am putting a big water-air coil over my existing hor air oil furnace
you need to start your figuring-out -- assuming that you are using your existing furnace blower to push the air-- with finding out how many cubic feet per minuts (CFM) that blower moves, and what amount of "back pressure" it can take (which will be a decimal of an inch of water column). Your furnace manufacturer's technical folks should be able to give you that data, like mine gladly did when I called them with the model # for my unit. I'll come back to those variables of CFM and back pressure further below-
then do a heat loss analysis on your house to see how many BTUs/hr you need for peak heating load- of if you are lazy and also confident that your existing furnace is not oversized (as in, it runs pretty steadily for long, long times during your occurrences absolute coldest weather, and doesn't do a lot of little intermittent brief and separate bursts of heat even in not-so-cold conditions) use its BTU/hr rating
then -- you'll want to talk with someone who is WAY more competent than a regular salesperson at sizing a coil to move the right number of BTUs, at the temperature of the water you anticipate as "normal" at your coil, at the CFMs moved by your blower, and with no more back pressure added by the coil than your blower can handle (and you want to err on the side of the lowest possible back pressure through the coil, because your ducts are already creating their own back pressure through the coil.
the assumption as to the water temp at the coil gets more complex if you are considering using heat storage or ever adding it in the future, as then you will need a bigger heat exchanger in order to be able to still extract enough heat from the stored water as it gradually cools
here are some threads with a photo of my coil and links to the folks who helped me size it and procure it. in my case, I have a BIG old farmhouse, so you probably can get by with way less coil; my coil also could've been smaller if I'd been planning to run without storage and known that my water would always be around 180
https://www.hearth.com/talk/threads/25090/
https://www.hearth.com/talk/threads/24899/
if the coil size you need to move the BTUs is bigger than your ducts, you could "funnel up" from the ducts to the HX, and then funnel back down from the HX back to the duct- just make the transitions as gradual/ tapered as you can for good airflow.
if time is abundant, you're handy with things, and budget is thin, you might be able to do something with good-sized car or truck radiator with a box built to match it to your ducts... just be careful that they're rated for the pressure you may be running your boiler system at
you'll also want the water-air HX on the "outlet" side of your furnace, as the electrical parts in your furnace are unlikely to be rated for entry/ ambient are much over 100degrees F- so putting an HX on the inlet side of your furnace blower would cook your furnace.
I don't have credentials, but your intake grille sounds inefficiently small to me and your whole system may run better if you are able to make the intake side of things less restrictive if you can do that without major disruption or cost
hope that all helps