for background, I'm going to be using 1200+/- gallons (6x6 ft square, 5 ft high) of unpressurized storage with a flat plate HX
I bought a bronze circulator (Wilo Star 21 BFX 3 speed) (Kind of Wilo's answer to the Grundfos 15-58) intending to use it on the "open" side to pump from the tank to the HX
and then I was reading some of the other threads here about people having circulator troubles, and a mention in particular of how unpressurized OWBs can tend to "go through" circulators if things are set up without an eye to avoiding cavitation, I got to wondering-- 'cause I really want to "do this once, and right" and minimize growing pains.
So I asked my vendor what the NPSH of the Wilo was, and he asked Wilo's tech folks, who responded with this:
"Regarding NPSHr curves for Star, no manufacturer publishes NPSH required for
wet rotor pumps, the reason being we are not concerned as much about
cavitation (boiling water at the eye of the impeller) but more concerned
about boiling the water (lubrication fluid from the system at the sleeve
bearings) in the rotor/can area.
70% of the motor heat is dissipated by the system fluid hence higher system
temps and higher motor heat amperage (larger wet rotor pumps) the faster the
lubrication fluid boils at lower temperatures.
This minimum inlet temp/pressure combination is always a higher pressure
than NPSHr so if the installation meets the "Minimum Inlet Pressure" as
indicated in our technical documents for sure it meets the NPSHr.
For example the Star Minimum Inlet Pressure is:
122 Deg F Min Press 0.7 PSIG
203 Deg F Min Press 4.4 PSIG
230 Deg F Min Press 14.7 PSIG
"
I'm aiming to push the tank to or as close to 200F as I can, for max BTU storage.
but, with a tank 5 ft high, and the circ mounted at the bottom of the tank, if I am doing my math right, I'll have only abiout 2psi of "head" from the weight of the water
so should I be looking at other circs that are non-wet-rotor, and/ or are designed to avoid cavitation even with very low inlet pressures?
if so, any suggestions as to a quality/ reliable/ long-lived one in bronze that won't break the bank any more than needed (I can wish, right?)
thanks, as always, for all the good knowledge, experience, and help 'round here
I bought a bronze circulator (Wilo Star 21 BFX 3 speed) (Kind of Wilo's answer to the Grundfos 15-58) intending to use it on the "open" side to pump from the tank to the HX
and then I was reading some of the other threads here about people having circulator troubles, and a mention in particular of how unpressurized OWBs can tend to "go through" circulators if things are set up without an eye to avoiding cavitation, I got to wondering-- 'cause I really want to "do this once, and right" and minimize growing pains.
So I asked my vendor what the NPSH of the Wilo was, and he asked Wilo's tech folks, who responded with this:
"Regarding NPSHr curves for Star, no manufacturer publishes NPSH required for
wet rotor pumps, the reason being we are not concerned as much about
cavitation (boiling water at the eye of the impeller) but more concerned
about boiling the water (lubrication fluid from the system at the sleeve
bearings) in the rotor/can area.
70% of the motor heat is dissipated by the system fluid hence higher system
temps and higher motor heat amperage (larger wet rotor pumps) the faster the
lubrication fluid boils at lower temperatures.
This minimum inlet temp/pressure combination is always a higher pressure
than NPSHr so if the installation meets the "Minimum Inlet Pressure" as
indicated in our technical documents for sure it meets the NPSHr.
For example the Star Minimum Inlet Pressure is:
122 Deg F Min Press 0.7 PSIG
203 Deg F Min Press 4.4 PSIG
230 Deg F Min Press 14.7 PSIG
"
I'm aiming to push the tank to or as close to 200F as I can, for max BTU storage.
but, with a tank 5 ft high, and the circ mounted at the bottom of the tank, if I am doing my math right, I'll have only abiout 2psi of "head" from the weight of the water
so should I be looking at other circs that are non-wet-rotor, and/ or are designed to avoid cavitation even with very low inlet pressures?
if so, any suggestions as to a quality/ reliable/ long-lived one in bronze that won't break the bank any more than needed (I can wish, right?)
thanks, as always, for all the good knowledge, experience, and help 'round here