Will you guys check my math.
Started burning 11/21 to today (2/10) = 82 days
Consumed so far this season of ~10-12% moisture content wood ~ 8.5 chords
20% MC Hickory or Oak per Engineering Toolbox ~3600 lbs/chord
Lbs consumed this season = 30,600 lbs
Per Siegenthaler's Training Doc 12% MC wood ~ 6800 btu/lb
Total BTUs this season = 30,600 lbs x 6800 = 208,080,000 BTUs = 208 MMBtus
BTUs/day = ~2.54 MMbtu
BTUs/hr = 105,700 btu/hr
So the magic number is ~106 kbtu/hr for a typical winter.
I assumed the Biomass 60's mean output at 180 kbtu/hr back when sizing components. Now with storage I can watch excess energy being accumulated by the tank temps. A cold day for us is 25-35F and on those days it takes quite a while to bring the bottom temp up. So I know with decent wood our 60 boiler stays ahead of the demand, but not with lots of excess energy. Don't have a more scientific way of estimating demand or do I have realistic load calcs on our leaky old house. Our propane furnace is a 175kbtu unit and it doesn't run continuously on cold days but pretty close to a 50% duty cycle, so it all seems to sync.
We're considering a lamba upgrade in the next few years and a pellet or ? within 6-8 years (age/health driven). There are some energy improvements we will be doing but now with storage I'd hate to go less than a 60 Class to have decent recovery times. Please let me know if you guys see any errors. Thanks
Started burning 11/21 to today (2/10) = 82 days
Consumed so far this season of ~10-12% moisture content wood ~ 8.5 chords
20% MC Hickory or Oak per Engineering Toolbox ~3600 lbs/chord
Lbs consumed this season = 30,600 lbs
Per Siegenthaler's Training Doc 12% MC wood ~ 6800 btu/lb
Total BTUs this season = 30,600 lbs x 6800 = 208,080,000 BTUs = 208 MMBtus
BTUs/day = ~2.54 MMbtu
BTUs/hr = 105,700 btu/hr
So the magic number is ~106 kbtu/hr for a typical winter.
I assumed the Biomass 60's mean output at 180 kbtu/hr back when sizing components. Now with storage I can watch excess energy being accumulated by the tank temps. A cold day for us is 25-35F and on those days it takes quite a while to bring the bottom temp up. So I know with decent wood our 60 boiler stays ahead of the demand, but not with lots of excess energy. Don't have a more scientific way of estimating demand or do I have realistic load calcs on our leaky old house. Our propane furnace is a 175kbtu unit and it doesn't run continuously on cold days but pretty close to a 50% duty cycle, so it all seems to sync.
We're considering a lamba upgrade in the next few years and a pellet or ? within 6-8 years (age/health driven). There are some energy improvements we will be doing but now with storage I'd hate to go less than a 60 Class to have decent recovery times. Please let me know if you guys see any errors. Thanks